10/15/2013 10:03 AM | |
Joined: 10/11/2006 Last visit: 9/5/2025 Posts: 6018 Rating:
|
Hello, if your encoder has no sense contacts, you have to bridge the sense terminal at the SMC20. Pin 1 to Pin 14 A controller compares the encoder system supply voltage - sensed via the Remote Sense cables - with the reference supply voltage of the encoder system, and adjusts the supply voltage for the encoder system at the output of the sensor module until the required supply voltage is obtained directly at the encoder system (only for 5 V encoder system power supply). |
With best regards, |
|
This contribution was helpful to
1 thankful Users |
10/25/2013 4:09 AM | |
Joined: 3/22/2013 Last visit: 6/10/2025 Posts: 12 Rating:
|
Thak you very much. |