11/3/2010 6:29 PM | |
Joined: 1/28/2009 Last visit: 7/11/2024 Posts: 6844 Rating:
Hello I used FB125 which prepared by siemens on aPROFIBUS DP configuration with ET200S as DP slave.I also checked module removal by this function , it is working.Check if this function supports your range of hardwares.Read the users' manual and check the sample set up.link regards |
11/4/2010 12:11 PM | |
Dear ste_angioni check this detailed description on "Reading out Diagnostic Data of ET200S- SFC13 / SFC59" . For more detail about these 2 function refer to this link(section 7.8 and section 13.4).I make copy of detailsabout data records (chapter 33) may you need to read diagnostic data, it is uploaded .I have done it for modules on ET200M,I think the principles are identical. check this link for a discussion on how detect slave failure on PROFIBUS DP subnet by help of SFC51. Best regards hdhosseini AttachmentData Record.zip (119 Downloads) |
11/9/2010 4:08 PM | |
Joined: 1/3/2009 Last visit: 6/30/2022 Posts: 161 Rating:
Hi,
The meaning of the data you will find in DR is explained in the attached pdf. AttachmentPages from s7sfc_en-EN.pdf (142 Downloads) |
Stefano Angioni |