2/23/2024 7:24 PM | |
Joined: 8/21/2020 Last visit: 2/26/2024 Posts: 2 Rating: (0) |
Hello, I try to communicate with LOGO via MTP panel, which is programmed using TIA portal. I have learned that for example AI1 address is defined in TIA as 3x300001 I need to learn how to call the VW addresses such as VW1 etc. I suspect that it is something like 4x400001 but can´t be sure. Mapping space range for VW is 0-850 and Mapping holding register space for that is between 1 to 425. Is there any appendix for interpreting the address spaces? In other words, I´d need an extension to the Modbus address spaces indicated in form 1x10000X, 3x30000X, 4x40000X. It would be very convenient and time saving as I must not find the right ones by trial and error. It would be greatly appreciated if a such table for address space conversions would be found. Here I do mean the fixed ones rather than the wild ones. Thanks, ------------------------------------------------------------------------------------------ |
Last edited by: The Helping Hand at: 02/26/2024 07:28:46New subject after splitting |
|
2/24/2024 3:17 AM | |
Joined: 12/18/2014 Last visit: 11/7/2024 Posts: 34159 Rating: (4254)
|
This address information is not available at LOGO! because LOGO! does not need it. In addition, Modbus at LOGO! is just a stripped-down Modbus. Edit: Take a look at this topic: Unified Panel to LOGO! Modbus ProtocolSpecifically the post by user Murof from 2/23/2024 7:52 AM. Maybe this user can help you. |
Last edited by: ixo65 at: 02/24/2024 03:34:04 |
|
2/26/2024 7:30 AM | |
Joined: 12/18/2014 Last visit: 11/7/2024 Posts: 34159 Rating: (4254)
|
The modbus addresses for VW0 to VW850 in LOGO! = HR1 to HR425 |