3/24/2009 9:38 PM | |
Posts: 2661 Rating:
|
Hi molon, For HART you need atleast V7.0 SP1 and IM's 153-2BA02/82-0XB0 must be used. See chapters 1.3.4 and 2.2.4 in the followingconfiguration note: Configuration of Redundant I/O Modules Regards |
3/25/2009 8:27 AM | |
Joined: 3/18/2009 Last visit: 5/6/2024 Posts: 306 Rating:
|
For the modules 331-7TF01 and 332-8TF01, in the HW config, you can 1. deactivate individual channels 2. enable or disable diagnostics for individual channels. As far as I know, you can avoid the alarms by either deactivating the channels or by disabling the diagnostic of that particular channel. My suggestion is to disable the spare channels for two reasons 1. to avoid the alarms 2. to decrease the cycle time of the AI or AO module, making the system response time more efficient. Also, you can useCiRto activate the channels when required in future. So to answer your question, I don't think you will need to connect any kind of resistors to avoid alarms. hope, this has helped. regards.
|
This contribution was helpful to
2 thankful Users |
11/9/2015 10:51 AM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4770 Rating:
|
New question published by nkr is split to a separate thread with the subject PCS7 V 8.1, hart modules with redundant controller. Best regards |