2/13/2013 12:49 PM | |
Posts: 87 Rating: (1) |
Help me! STEP7 detetct error in DP slave.... But I dont underatsnd why.... I have CPU315 v3.2 but in step I put v3.1 (I dont use special functions). All CPU stay in STOP (((( Attachment2044_Tash_PLC_TEST.zip (75 Downloads) |
Last edited by: andrewF at: 2/13/2013 1:13 PMLast edited by: andrewF at: 2/13/2013 12:50 PM |
|
2/13/2013 1:24 PM | |
Posts: 366 Rating: (30) |
You have to make an Hardware-Update. You're not allowed to have another version number on your CPU than in your hardware configuration! Best regards |
2/13/2013 1:46 PM | |||||
Posts: 87 Rating: (1) |
I cant Instal needed HSP - I have STEP v5.4 and I not have config in HardwareMan CPU ver v3.2 But I want use this help https://support.automation.siemens.com/WW/llisapi.dll?func=cslib.csinfo&lang=en&objid=46119963&caller=view and I want use this CPU with this recomendations: Configuration with older software versions: If the new functions are not required, you can configure the module in STEP 7 as predecessor (FW V3.1) with the latter's scope of functions.
I not have possibility use STEPv5.5 |
||||
2/13/2013 2:14 PM | |
Posts: 366 Rating: (30) |
Ok looks like you can do it in this way. And what kind of fault you have on a DP-Slave? is there anywhere a red LED lightening? What says diagnostic?? |