9/6/2022 9:50 AM | |
Joined: 10/11/2006 Last visit: 7/12/2024 Posts: 5874 Rating:
|
Hello, I think you chose a self-ventilated 1LE1. With the self-ventilated motor, the fan sits on the rotor and also slows down at lower speeds, thus reducing the cooling of the motor. Therefore, the motor characteristic curve of the self-ventilated motor is reduced at low speeds in contrast to the externally ventilated motor. When you change in SIZER the cooling method of the motor to "force-ventilated" (option F70), you get the motor characteristic without derating at low speed. Please look at catalogue D81.1, page 1/80, too.
|
With best regards, |
|
This contribution was helpful to
1 thankful Users |
Follow us on