I have another issue. I have 1 Engineering Station and 2 OS Single Stations. I will be using IPC 547G with CP1623 for all three. For my 2 OS Single Station will I insert SIMATIC PC Station, OS or OS Client? Also when configuring these OS Single Station will I use WinCC Application or WinCC Application Client? Thankyou ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 05/14/2020 14:17:11New subject after splitting |
|
5/14/2020 2:26 PM | |
Joined: 3/14/2008 Last visit: 10/15/2024 Posts: 2111 Rating: (942)
|
Hi, Please check the PCS7 Standard Architecture document, showing you different kind of setups. You can have a redundant OS Single Station as well. Or instead of using 2 Single Station, use one station and define the other as OS client. It depends how you wanna work with it. In general, you will get OS Single Station licenses and are defined as server, so Simatic PC Station OS and WinCC Application should be used. For clients, use WinCC Application Client. |