12/31/2020 8:04 PM | |
Joined: 12/11/2019 Last visit: 8/22/2022 Posts: 10 Rating: (0) |
Can you guide me how to configure modbus for both cp-8050 & 8021. I am solar substation here relays and MFM devices were communicating modbus. please kindly guide me. that would be much helpful for us in site commissioning. if any documentation are there also please share.
------------------------------------------------------------------------------------------ |
Last edited by: ajeesashi95 at: 12/31/2020 20:09:40Last edited by: CS Moderator at: 01/03/2021 11:05:45New subject after splitting |
|
1/4/2021 4:30 AM | |
Joined: 10/7/2005 Last visit: 9/16/2024 Posts: 3020 Rating: (1054) |
While I can't offer any hands-on experience, chapter 13.8 of the 1860 page long SICAM CP-8050 manual seems to have more than enough details on its Modbus capability and configuration. The same also applies for chapter 12.9 of the 1924 page long SICAM CP-8021 manual. |
Cheers |
|
1/24/2021 4:01 PM | |
Joined: 9/27/2006 Last visit: 9/16/2024 Posts: 12282 Rating: (2683) |
Hello ajeesashi; As I am not very familiar with SICAM RTUs, I can only offer these links: - Sicam A-8000 series, manual CP-8050 https://support.industry.siemens.com/cs/ww/en/view/109757272 Chapter 13 gives a good description of the implementation of Modbus RTU on this CP, however, as shown in the screenshot below, you require an additional software tool to select and format the data you will request from a Modbus slave. One of these tools I have located on the web is the SICAM Toolbox II: Hope this helps, |
Last edited by: dchartier at: 01/24/2021 16:13:39 |
|
Follow us on