Hi all, I think I have similar issue, where I cannot get the right time displayed on my HMI. In TIA portal vs 15 in online and diagnostics window of PLC (s7-1200) I set module time by taking it from PG/PC. In module config day light saving time is now unchecked just to be sure that it does not complicate things, however even with this checked I get the exact same thing.
My laptop is set to UTC+0, as I live in UK. Then I use and Rd_Sys_time, and Rd LOc time they both show one hour less then the above mentioned module time. Consequently when the HMI shows wrong time too. Please see attached screen shot. Any insight would be appreciated. Best Regards, Peter ------------------------------------------------------------------------------------------ |
Last edited by: The Helping Hand at: 10/07/2019 15:05:16New subject after splitting |
|
10/9/2019 12:14 AM | |
Joined: 7/7/2010 Last visit: 7/12/2024 Posts: 14948 Rating: (2393)
|
How is the s7-1200 configured for summer hours? If it's configured to never change, the 1-hour time difference should go away between local and system time.
|
science guy |
|
This contribution was helpful to1 thankful Users |
10/10/2019 9:27 AM | |
Joined: 3/9/2018 Last visit: 12/1/2020 Posts: 10 Rating: (0) |
Hello, you are probably right, however I will have to confirm this after my next visit to this plc. Thanks!! Peter |