I have local module error , but i dnt have anything below. Anything in forced values. Some suggestion ? ------------------------------------------------------------------------------------------ |
Last edited by: The Helping Hand at: 12/05/2023 15:08:34New subject after splitting |
|
12/5/2023 3:40 PM | |
Joined: 7/7/2010 Last visit: 9/12/2024 Posts: 15180 Rating: (2417)
|
It helps to look in the PLC diagnostics buffer for the red check boxes without matching green check boxes later that means the error already cleared. Also, expanding devices showing as RED or not fully GREEN to show the options for viewing that specific device or module online and diagnostics data is helpful as well.
|