10/5/2006 10:14 AM | |
Posts: 661 Rating: (123) |
Hi, yes, you can connect LOGO! power pallel to get more current. Here are more informations: http://www.automation.siemens.com/sitop/html_76/logopower.htm Which version of LOGO! power you need depends on the current your loads/motors are working with if you also want to supply them with LOGO! power. Anyway the basic- and extension modules work with little current (mA). Have a look at the technical data of the manual. So you´ll have to calculate how much current your loads will need. But also a question to you: Do you know that LOGO 24RC has no analog inputs at the basic module opposite to the 12/24RC-version? If you want to connect analog sensors (e.g. for rain or light) you will have to buy extensions ... Regards Fux |