2/20/2017 12:35 PM | |
Joined: 3/2/2007 Last visit: 7/26/2024 Posts: 932 Rating: (5) |
what is the maximum permissible cable size mm2 for following 3VT circuit breakers connection. the catalogs and manuals do not clearly indicate this info. thank you breaker 1 : 3VT3763-2AA36-0AA0 + 3VT9331-6AB00 breaker 2 : 3VT1712-2DA36-0AA0 |
... thank you ... |
|
2/21/2017 4:19 PM | |
Joined: 3/2/2007 Last visit: 7/26/2024 Posts: 932 Rating: (5) |
we just need to check the permissible cross-section for each one, before getting the copper cables. in the below link on pages 3/11 and 1/12, there is tables "Recommended cross-section of cables". which data is for the two breakers below? breaker 1 :3VT3763-2AA36-0AA0+3VT9331-6AB00 breaker 2 :3VT1712-2DA36-0AA0 |
Last edited by: Ziemens at: 2/21/2017 4:21:16 PMLast edited by: Min_Moderator at: 2/21/2017 4:45:46 PMEdit link ... thank you ... |
|
2/22/2017 11:28 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (876) |
Hello, 3VT3763-2AA36-0AA0 - Circuit breaker rated capacity is 315 Amp (I presume since ETU selection capacity is 315) 3VT9331-6AB00 - Is ETU rated capacity is 315 Amp. Select copper cable of size 185 sq mm 3VT1712-2DA36-0AA0 - Circuit breaker capacity is 125 Amp Select copper cable of size 70 sq mm. HTH. |