7/5/2024 8:24 AM | |
Joined: 6/19/2019 Last visit: 10/29/2024 Posts: 705 Rating: (76) |
Hello i think you need open MB_COMM_LOAD_DB and there you can find some parameters you can try to play with them like RESP_TO (Response timeout:Time in milliseconds allowed by "MB_MASTER" for the slave to respond. If the slave does not respond in this time, "MB_MASTER" repeats the request or terminates the request with an error if the specified number of retries has been sent.5 ms to 65535 ms (default = 1000 ms). you can try like 333ms (3 times faster for get error signal) then there also is RETRIES (defaut is 2) maybe you can set to 1 |
Last edited by: Mr.V at: 07/05/2024 08:30:46 |
|
7/6/2024 1:40 PM | |
Joined: 3/29/2023 Last visit: 10/15/2024 Posts: 36 Rating: (0) |
Hello thanks for replying, today i tried what you suggest (RESP_TO changed from 1000 ms to 333 ms and retries was 0 by default) , nothing changed still if i not skip the address that is turned off RX/TX blinking so slowly and all drives gives comm overtime Any ideas |
Follow us on