Joined: 9/27/2006 Last visit: 11/18/2024 Posts: 12296 Rating: (2691) |
Hello AhmetTan; There are 2 issues I can see here: First, with the demo software of Open Modbus TCP, the SF LED will keep blinking until the license is installed (see Weustenraeuber's posts in the foolowing thread); but communications will work if properly configured, as Kaulquappe has pointed out. /tf/WW/en/Posts/47318 Second, an "Area length error" error message means that you are trying to reach an address that doesn't exist, that has not been configured or that cannot be reached at the present time. So check your porgram, there has to be an addressing error somewhere. Hope this helps, Daniel Chartier |