You can do a PPI network with the 5x 221 and 5x TD200. The 5x 221 can be a slave if no communication between the PLC's is required. The 5x TD200 are a master in the network. To get the same information like the TD200 display in a PC you can use the S7-200 OPC-server "PC Access". Use PC-Access as a master and do the communication via the USB/PPI-cable (it's a multi master cable). More information about a PPI network and PC-Access in the PPI network you will find in the internet: http://support.automation.siemens.com/WW/view/en/21063680 You can find all needed products in the A&D mall https://mall.automation.siemens.com |