3/28/2012 2:38 PM | |
Joined: 9/27/2006 Last visit: 7/22/2024 Posts: 12270 Rating:
|
Hello krishnakumar; Tibi68 is right, the only way you can setup a ring topology over Profibus is by using OLMs (Optical Link Modules). Have a look at the contents of the following FAQs: How do you set up a redundant optical ring with PROFIBUS OLMs? How do you set the DIP switches on the PROFIBUS OLM in order to achieve a line topology, a star topology or a redundant optical ring? How do you set up a redundant optical ring with two OLMs and what LED display behavior is to be expected? And also studythis manual (look at the chapter on topology): SIMATIC NET PROFIBUS, Optical Link Module, OLM / P11 V4.0, OLM / P12 V4.0, OLM / P22 V4.0, OLM / G11 V4.0, OLM / G12 V4.0, OLM / G22 V4.0, OLM / G12-EEC V4.0, OLM / G11-1300 V4.0 OLM / G12-1300 V4.0, Operating Instructions Hope this helps, Daniel Chartier |
This contribution was helpful to
1 thankful Users |
3/28/2012 5:33 PM | |
Joined: 1/15/2009 Last visit: 4/19/2024 Posts: 316 Rating:
|
Yes, you definitely cannot loop the last node to the first node in profibus. I created a sketch here that shows how you can run your profibus (both copper and fiber) and where the terminations go. I apologize as my handwriting and art skills are not very good (probably why I gravitated to engineering The box that shows the terminators, are active terminators. I prefer these for terminations to the switch on a profibus connector. Attachmentprofibus chain.PDF (103 Downloads) |
The best location for all PCS 7 content (manuals, guides, application notes, FAQs, and videos). |
|
This contribution was helpful to
1 thankful Users |