1/11/2010 8:56 AM | |
Joined: 1/4/2007 Last visit: 7/11/2024 Posts: 1134 Rating:
|
Hello Alexander Top, The RS-232 protocol is described into the manual of the Siwarex M module, but it is the same as for the Siwarex U module. Please take a look into the attached file. If you only need the weight value of the Siwarex U module, I recommendyou to use the TTY interface of the Siwarex U module. The TTY protocol is much more easier than the RS-232 protocol. By using the TTY protocol you need a TTY-RS232 interface converter. Let me know, if you are interested in that TTY-protocol. Best regards Siwarexi AttachmentRS232_protocol.pdf (340 Downloads) |
1/12/2010 11:29 AM | |
Posts: 2 Rating:
|
Thank you for the file. I think about the TTY protocol, but it may be that I need configure Siwarex U. And can you help me with TTY protocol? |
1/13/2010 11:42 AM | |
Joined: 1/4/2007 Last visit: 7/11/2024 Posts: 1134 Rating:
|
Hello Alexander Top, Attached you can find the TTY protocol: The Siwarex U module is sending permanently the “Gross value channel 1”, “Specified value 1”, “Gross value channel 2” and “Specified value 2” (See also the page 11-5 of the attached file). You are right: If you want to use the TTY protocol, you have to configure one-time the Siwarex U module. Best regards Siwarexi AttachmentSiwarex_U_TTY_en.pdf (324 Downloads) |
Follow us on