1/27/2014 1:49 PM | |
Joined: 5/12/2006 Last visit: 10/17/2024 Posts: 22420 Rating: (3020)
|
Hello, have you chance this parameter online or offline? Regards Christoph |
1/27/2014 1:55 PM | |
Posts: 11 Rating: (0) |
I have tried to change them in both, online and offline. None of them work. Regars Ludo |
1/27/2014 2:04 PM | |
Posts: 21 Rating: (1) |
hi if you have the swich on inhibiat and ready to switch on please check the p9 and p10 |
1/27/2014 2:08 PM | |
Posts: 11 Rating: (0) |
P9 is set to reade. But P10 is set to quick commissioning. But I cant change it to ready. I don't know why. Any ideas? |
1/27/2014 2:14 PM | |
Joined: 5/12/2006 Last visit: 10/17/2024 Posts: 22420 Rating: (3020)
|
Hello, set p212.1 = 1 p210 = 345 p340 = 1 Regards Christoph |
1/27/2014 2:28 PM | |
Posts: 11 Rating: (0) |
thanks that worked well and any idea what to do with p010 parameter? |
1/27/2014 2:32 PM | |
Joined: 5/12/2006 Last visit: 10/17/2024 Posts: 22420 Rating: (3020)
|
Hello, set p10 = 0, get you an error ? Check the Alarm windows ! Regards Christoph |
1/27/2014 2:37 PM | |
Posts: 11 Rating: (0) |
yes I after i set it 0 the Alarm 7950 will occur. Drive incorrect motor parameter (parameter 311). |
1/27/2014 2:43 PM | |
Joined: 5/12/2006 Last visit: 10/17/2024 Posts: 22420 Rating: (3020)
|
Hello, ok which motor do you have? and which value do you have set in p311? Regards Christoph |