8/29/2020 8:48 PM | |
Posts: 4 Rating:
|
Dear sir,.. In our s7 300 plc We are facing problem sometimes..like 4hrs once or 8 hrs once.. Some outputs are not stopping, like belt ,coveyor and weigh feeders are stopping suddenly without any fault. And i also checked in RIO panel there no fault in any module or ET200 Then we checked the CPU diagnostic buffer .. We are getting two information one is in log 10 is saying I/O access error Plz give the solutions and I have attached photo of it ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 08/31/2020 11:25:31New subject after splitting |
|
8/29/2020 8:55 PM | |
Posts: 4 Rating:
|
Another one is Rack failure.. I m waiting for solution..for this plz can any one help on this ..problem.. |
8/31/2020 11:50 AM | |
Joined: 9/27/2006 Last visit: 7/14/2024 Posts: 12268 Rating:
|
Hello Tippesh; You have identified the I/O station giving you trouble. What family is this station, ET 200S, ET 200M... or tell us the part number of the head module (IM 153-2, for example). Do any of the I/O modules have a diagnostic LED active on the front?, which module number and which LED? Assuming this is a Profibus network (you haven't mentioned it yet) that gives you unpredictable glitches, try applying the suggestions in this article: https://us.profinet.com/top-5-reasons-your-profibus-network-failed/ Hope this helps, Daniel Chartier |
9/1/2020 11:15 PM | |
Joined: 9/27/2006 Last visit: 7/14/2024 Posts: 12268 Rating:
|
Hello Thippesh; Read this thread from the beginning once more, you will see there are 2 mechanisms we have used to troubleshoot your problems: - diagnostic LEDs on the CPU, the interface modules (the IM 153-1) and the I/O modules in the remote rack. - the contents of the diagnostic buffer, especially the module addresses of the faulty equipment. You could also check out the online view in HWConfig, faulty stations will appear with a fault icon, clicking on that icon will open the local diagnostic buffer of the modules, containing local fault information. You have to learn to use these troubleshooting tools, and to interpret the information provided there. Chapter 23 "Diagnostics" of the Programming with Step 7 manual is a very informative source you should look at. https://support.industry.siemens.com/cs/ww/en/view/45531107 Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 09/01/2020 23:20:36 |
|