7/21/2014 11:35 AM | |
Joined: 2/18/2013 Last visit: 7/11/2024 Posts: 139 Rating:
|
Hello! I have communication problem with my PC and CU (310-2DP) via PROFIBUS. I use STARTER Project Wizard - >Find drive units online... -> Set and test PG/PC interface (All OK). But next step return an error "No devices have been found". Please help.
AttachmentS120.zip (448 Downloads) |
7/21/2014 12:18 PM | |
Joined: 2/18/2013 Last visit: 7/11/2024 Posts: 139 Rating:
|
ChristophD, I have set DEVICE as Access point, but no result (( |
7/21/2014 12:54 PM | |
Joined: 2/18/2013 Last visit: 7/11/2024 Posts: 139 Rating:
|
1. Screenshot in attachment. 2. The Option "only master on the bus" is set 3. STARTER 4.3.1.0
|
7/21/2014 1:46 PM | |
Joined: 5/12/2006 Last visit: 7/15/2024 Posts: 22312 Rating:
|
Hi, sorry but you have no SSP for a CU310-2 DP installed. The FW for CU310-2 DP is starting with V4.x not with V2.x. In the CF Card of the CU310-2 DP is a file Content.txt, here is the FW listed which is on the FW. The SSP you can download here: http://support.automation.siemens.com/WW/view/en/97044475 Regards Christoph |
This contribution was helpful to
2 thankful Users |
7/21/2014 2:10 PM | |
Joined: 2/18/2013 Last visit: 7/11/2024 Posts: 139 Rating:
|
Yes I have installed SSP for my CU. All work fine! Thank You! |
This contribution was helpful to
1 thankful Users |
Follow us on