2/4/2019 1:55 PM | |
Joined: 6/4/2010 Last visit: 9/30/2024 Posts: 387 Rating: (128)
|
Dear forum member, The "Storage is not active" message is shown,when the storage is configured in the archive group of the project, but it is in the OFF state (SMC). Please turn it on. See attached snap-shot. The second issue may be related to the FAQ 109760471: https://support.industry.siemens.com/cs/ww/en/view/109760471 (for Extranet users only): Memory limit of Report Manager Windows 10 Feature Pack 1803 reserves more memory for 64 bit processes than prior releases. Therefore it is required to set the memory limit of the Report Manager to at least 6 GB. Otherwise the Report snapshot creation might fail and the system reports that not enough memory is available e.g. when executing a report or retrieving log data. Please note that this value must be changed only if the value is lower than 6 GB as e.g. as our default value of 4 GB. It may also be noteworthy that the memory limit must only be increased to 6 GB for installations < V3.0 SR4. The memory limit of the Report Manager is located in the Management View below the Server object. Best regards, Albis |
Last edited by: Albis at: 2/4/2019 1:57:54 PM |
|