With the LWE V1.0.x, the via Parameter-VM-Mapping transferred words (VWx) in the LWE still had to be broken down into their bytes for entering the switch-on and switch-off times and separate input fields had to be created for hours and minutes and then the HEX data format to get voted. This is no longer necessary with the current LWE V1.1.0. There you can use the "ScaleTime" function and select the "Weekly (time)" format for the "Time" parameter. So is only one I/O field needed.