hello, I have a similar question I have a system that is a PC with wincc flexible 2008 runtime and S7-200 plc. The connection available is only one (don't know why). I can't even be with wincc flexible and microwin at the same time connected. But they asked if there's a chance to install a panel in the field. Can I setup a server-client configuration with wincc flexible or can I use OPC server in one runtime and OPC client in panel to transfer all the data and commands? ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 7/22/2016 1:27:19 PMNew subject after splitting |
|
7/22/2016 5:15 PM | |
Joined: 5/28/2008 Last visit: 11/6/2024 Posts: 4516 Rating: (839) |
Hello, All Basic or Comfort Panels can be connected to S7-200. Please check your interface as some panels have only PN interface and you did not told us if you have Ethernet CP in S7-200 or not. Hope this helps. |
Ayman Elotaify |
|