7/14/2022 8:05 AM | |
Joined: 10/11/2006 Last visit: 9/5/2025 Posts: 6038 Rating:
|
Hello, <TO>.Modulo.length (Restart) You can change the value with "WRIT_DBL"-command. After this you have to restart the TO. The Axis must be disabled. There are other possiblities, to change the relationship between Master and Slave. 9.1.7 MC_CamIn V6 (S7-1500T) MasterScaling/SlaveScaling 9.1.2 MC_GearInPos V6 (S7-1500T) RatioNumerator / RatioDenominator https://support.industry.siemens.com/cs/ww/en/view/109781851 |
With best regards, |
|
8/3/2022 1:41 PM | |
Joined: 11/4/2011 Last visit: 8/28/2025 Posts: 276 Rating:
|
Hey there, I found that there is also a very new FAQ that shows just what you ask for: https://support.industry.siemens.com/cs/ww/en/view/109810890 So in case anybody has a similiar question -> check the FAQ, this shows what to check and what to do. Regards, |
This contribution was helpful to
1 thankful Users |
3/20/2025 2:59 PM | |
Joined: 4/28/2015 Last visit: 8/21/2025 Posts: 3 Rating:
|
Dear Daviso ,Dear David: I also had encounted this problem recently, edited this process for "WRIT_DBL" according to "109810890"FAQ. it seemed that the "SRCBLK" data type did not be support, i do not know where is the problem “error no.16#8093" from. SIM:PLCSIM advanced v4.0 CPU:S1515T No data block or a data block that is not in the work memory is specified for the SRCBLK parameter.
|