6/26/2012 8:16 PM | |
Joined: 1/28/2009 Last visit: 8/31/2025 Posts: 6874 Rating:
|
Hello, Check the attachment and the following examples: [code]// L PIW 200 // T MW 200 //copy the analog signal ////////////////////////////////// L MW 200 ITD DTR L 2.764800e+004 /R L 1.000000e+002 //range 0 to 100 *R T MD 50[/code] and this solution with FC105: [code] CALL "SCALE" IN :=MW200 HI_LIM :=1.000000e+002 LO_LIM :=0.000000e+000 BIPOLAR:=FALSE RET_VAL:=#ret OUT :=MD50[/code] attachment is only added to give you insight of digital representation of analog signals to their digitalized counterpart values.Full text here(section 5): http://support.automation.siemens.com/WW/view/en/8859629 Hope this helps Best regards Hamid Hosseini |