Hello Will; Did you really meana Sitrans LU250 HART, or did you mean a Sitrans LU250 Profibus-PA? If you want to use HART communications, you would need the following HART input module, and it can only be mounted on a Profibus-DP slave station (ET 200M):
If you do intend to use Profibus-PA in your project, please look at the recent thread giving abasic overview on connecting PA instruments to a DP-master: In the meantime you could look at the manuals for both types of intrument, so you can see the differences between the two (as far as communications with the PLC): SITRANS LR250 (HART) - Operating Instructions SITRANS LR250 (PROFIBUS PA) - Instruction Manual Hope this helps, Daniel Chartier |
||
| 6/19/2014 10:26 PM | |
|
Posts: 2 Rating:
|
thanks sir, very helpful info |
| 6/24/2014 9:55 AM | |
|
Posts: 124 Rating:
|
For the Profibus PA versions, there is also a application guide in the internet. Maybe this is also helpfull for you. Here the link ==> http://www.automation.siemens.com/mcms/sensor-systems/SiteCollectionDocuments/pi/application_guides/en/AG060417.pdf Cheers Levelmans |