(0)| 2/18/2012 10:09 AM | |
|
Joined: 8/18/2009 Last visit: 7/28/2025 Posts: 558 Rating:
|
Please tell me which current value we should consider during panel designing... |
|
Rajkiran Patil |
|
| 2/18/2012 10:29 AM | |
|
Joined: 5/28/2008 Last visit: 1/3/2026 Posts: 4522 Rating:
|
Hello, According to technical specifications in thislink, input current at 230 VAC is 0.5 Amps. So, if you will use this voltage selection, you have to use a MCB with rating greater than 0.5 A. 0.63 or 1 A will be fine. And for inrush current, it is stated in the technical specifications 63A;Full width at half maximum 1 ms, and of course MCB should not have enough time to trip (only 1ms). Hope this helps.
|
|
Ayman Elotaify |
|
This contribution was helpful to
|
|
| 2/21/2012 5:55 PM | |
|
Joined: 7/2/2008 Last visit: 12/21/2025 Posts: 929 Rating:
|
Hello RAJKIRAN, For heat calculation you should use the power loss which actually is the heat dissipation. The power loss of6ES7407-0KA02-0AA0 is 20 W. Best regards. H-H
|