Joined: 8/31/2005 Last visit: 8/20/2024 Posts: 2198 Rating: (328)
|
Hello ram535, the only thing I found is your firmware version of the sinamics. Did you install this SSP? If this did not help you should make a support request. |
|
|
1/27/2011 10:33 AM | |
Joined: 8/31/2005 Last visit: 8/20/2024 Posts: 2198 Rating: (328)
|
The alm_control you can find here. But in your component list is a SLM, not an ALM. But maybe the newer SLMs are controlled the same way, and I'm not shure that it is, what your support guy ment.
Here is a FAQ/guide, how to connect a S120 to a T-CPU (see chap 1.4 and 6.4, without a TB30 you may set p864 to a fixed "1" , when making the BICO connections.) I think your SLM has a DriveCliQ connector,I do not know if it transfers the signals over it. This manual describes the same. I am wondering why you get a PROFIBUS fault, when the power supply seens to have a problem. What is your actual problem? The PROFIBUS fault, or why you can't enable the axes? |
Last edited by: miami at: 1/27/2011 10:52 AMLast edited by: miami at: 1/27/2011 10:42 AM |
|
1/27/2011 6:02 PM | |
Posts: 11 Rating: (0) |
I change p864 to 1 and now i can start the motor from my program. Thank you for everything. |