7/9/2009 10:23 AM | |
Posts: 272 Rating: (4) |
It seems that this happened on a already running system, please check the system configurator properties and see is it linked to your proj. |
7/10/2009 2:57 AM | |
Posts: 2661 Rating: (279)
|
Hi NimaMoaddeli, This behavior is because of the faceplates in the Water Library. I installed WL, tested and had the same problem! The solution is change the block name in CFC to MOTORand it'l work! This is only for W_MOT1, I haven't tested other blocks. This kind of block naming is probably Water Library naming convention, I haven't had time to read the manual. Looks like (the Water Library is) an interesting product... See attached screenshot. Regards AttachmentW_Mot1.pdf (212 Downloads) |
Last edited by: Phantom75 at: 7/10/2009 10:01 PMLast edited by: Phantom75 at: 7/10/2009 3:01 AM |
|
This contribution was helpful to1 thankful Users |
7/10/2009 9:24 AM | |
Posts: 272 Rating: (4) |
where do we use water lib?? |
7/10/2009 10:30 PM | |
Posts: 2661 Rating: (279)
|
Hmm...That's strange. The name of the W_MOT1 block in the CFC has to be changed to MOTOR (see Fig1 in screenshot). The CFC has to be compiled and downloaded. The OS has to be compiled and downloaded if on a server. Ifthis screen isalready open in runtime, you should flip screens for an update. If nothing works try to see the message in the apdiag window when you click on the W_MOT1 block icon.Export this message and post in your reply. See Fig2, Fig3 and Fig4 on how toactivate the apdiag. Attachmentapdiag help.pdf (92 Downloads) |
Last edited by: Phantom75 at: 7/11/2009 7:23 AM |
|
This contribution was helpful to1 thankful Users |
Follow us on