11/16/2015 3:46 PM | |
Posts: 58 Rating:
|
Hello, Function parameter for selecting a setpoint and command source which is to be parameterized when a quick parameterization (P370) is carried out. 0 = PMU 1 = Analog input and terminal strip 2 = Fixed setpoints and terminal strip 3 = Motor operated potentiometer and terminal strip 4 = USS 5 = SIMOLINK (cannot currently be implemented) 6 = PROFIBUS (CBP required) 7 = OP1S and fixed setpoints 8 = OP1S and motor operated potentiometer Notes: During converter initialization, a parameter error may be displayed if the parameter does not correspond with the factory setting P366: P366 P368 =0 =0...8 =1 =7 =2 =7 =3 =0 =4 =8 >4 =0...8 If the values do not correspond, P368 has to be adapted (in P60=3) |
11/18/2015 7:41 AM | |
Joined: 9/16/2013 Last visit: 11/12/2023 Posts: 145 Rating:
|
Hello sam2014, you should P53=7 P060=5 P918.1=profibus address P060=7 then you the communication between drive and plc are ok,and you can enter the rest of parameter like: p100=control mode p443= main setpoint source p554.........p564=control word1 about the P734 = Received Data From Drives to PLC p734.1= k0032 receive status word1 p734.2= k0034 receive status word2 p734.3= kk0148 receive speed/actual value. may be the attached doc could help you. Best regards hag010 Attachmentvc332_kompend_kap06_e.pdf (607 Downloads) |
11/18/2015 1:31 PM | |
Joined: 7/30/2014 Last visit: 7/20/2025 Posts: 155 Rating:
|
Hello, Thnx for all answers, I shall try it. Best regards |
Follow us on