Hello Dadoui It is possible to have a connection between a S7-300 and a WinCC Flexible using Ethernet Point to Point Modems. We have once done communication between a IM151-8 PN/DP and a TP177B HMI panel using "Smart Bridges" Wireless point to point connection Radio-Modems. As long as you can ping the PLC from the HMI side, you can make a connection. The Bandwidth is limited so update times may be slow. Hope this helps Cheers Navnag |
There is no such thing as the last bug in a program |
|
5/28/2014 1:44 PM | |
Posts: 1368 Rating: (126) |
..And here you find an application for a VPN tunnel over radio network.... http://support.automation.siemens.com/WW/view/en/24960449 |
5/28/2014 1:52 PM | |
Posts: 25 Rating: (0) |
I configured blocks of sending dataspecific toEthernet (FC 5 AG_SEND) in S7-300 to tags in WinCC but how these data will be received in WinCC? is there any configuration to do in WinCC or I just need to specify ethernet link in the communication area (attachment)?
Attachmentdocc.pdf (250 Downloads) |
5/28/2014 10:08 PM | |
Joined: 4/19/2008 Last visit: 2/9/2024 Posts: 1525 Rating: (159) |
Hello Dadoui, Look at the FAQ, How do you configure a connection between WinCC flexible Runtime (PC or Panel) and a SIMATIC S7-300 / S7-400 via Industrial Ethernet? Follow the Step's mention in that, then tell us whats wrong you have done..... |