10/13/2008 7:46 PM | |
Posts: 24 Rating: (0) |
Making commissioning in Rabigh cement plant, two of our MM440 for belt conveyor giving F0022 with code 12. This happen after finishing our trial run for four hours. Can somebody advice the reason for this kind of fault and the corrective action necessary to prevent it when we replaced it with new one. The MM440 is having an output choke and input choke with option PROFIBUS module. F0022 comes out after closing the contactor for maininput supply, without giving on command. Appreciate if anybody could help us, were in tight schedule to give an answer to customer. Regards, Updated - Please see the attachment for the solution. From RicoT of Siemens Limited Saudi Arabia AttachmentF0022.pdf (272 Downloads) |
Last edited by: RicoT at: 10/17/2008 6:59 AMLast edited by: RicoT at: 10/13/2008 7:49 PM |
|
10/13/2008 10:42 PM | |
Posts: 1064 Rating: (72) |
/tf/WW/en/Posts/7328 this link and see if it helps, f0022 could be caused by a loss phase or motor grounded |