Joined: 5/6/2010 Last visit: 10/14/2024 Posts: 1984 Rating: (278) |
Hello HBCM_, which PLC do you want to use? This is important for any suggestion. regards |
2/25/2020 4:49 AM | |
Joined: 10/7/2005 Last visit: 10/14/2024 Posts: 3024 Rating: (1054) |
It seems to be saying -31663 based on HBCM_'s screendump. That then would be 8451(hex) as the error code which - as per HTA Instruction help - means "Non-supported data type in the OUT parameter". Can't argue with that one as a DWORD is used by HBCM_ for the OUT parameter whereas the HTA help insists that "You can reference the following data types using the pointer in the OUT parameter (ASCII): STRING, WSTRING, Array of CHAR, Array of WCHAR, Array of BYTE, Array of WORD" |
Cheers |
|