6/23/2021 2:10 PM | |
Joined: 12/18/2014 Last visit: 9/11/2025 Posts: 35953 Rating:
|
For testing which on which AI the PT is, you can use the display of the LOGO!. Press cursor down button so often until you see the start screen. Then press the cursor right button so often until you see the screen 3/9 (for AIs 1-5). On this screen you can see which AI has the value of the PT. 25 °C is around 300 units. AttachmentLOGO! 8 manual 0BA8 2017_11 xxxx8-0BA0 page 354.pdf (516 Downloads) |
6/23/2021 2:12 PM | |
Joined: 2/22/2008 Last visit: 4/25/2025 Posts: 2698 Rating:
|
Sorry, but that's wrong, with 0 AI the AM2 RTD starts with AI1, with 2 AI the AM2 RTD starts with AI3, with 4 AI the AM2 RTD starts with AI5. Try attached program only for testing your analog input, AI1 should display the right value. If not, then there is something wrong with the wiring. Regard, Scorp AttachmentPT1000-Test.zip (500 Downloads) |
6/23/2021 8:39 PM | |
Joined: 12/18/2014 Last visit: 9/11/2025 Posts: 35953 Rating:
|
But he has a AM2 RTD. |
6/24/2021 10:07 PM | |
Joined: 2/22/2008 Last visit: 4/25/2025 Posts: 2698 Rating:
|
If you have a multimeter, just measure the resistance of the PT100 or PT1000, with is not connected to the AM2 RTD. PT100 has 100 Ohm at 0°C, PT1000 has 1000 Ohm at 0°C. Other resistance thermometers should have other values. See on https://en.wikipedia.org/wiki/Resistance_thermometer for more details, also for a little table showing the resistances of different thermometers for different temperatures. Regards, Scorp |