9/10/2014 8:21 PM | |
Posts: 784 Rating: (52) |
Hello, Perhaps this link might help. Best regards...... |
9/11/2014 9:27 AM | |
Joined: 10/14/2011 Last visit: 3/27/2024 Posts: 38 Rating: (1) |
Dear Experts, 1- Our PLC is 417-4XT05-0AB0 with MC SRAM 4MB 6ES7 952-1AM00-0AA0(THIS MEMORY CARD IS RAM AS IT IS SHOWING IN SIEMENS DATA SHEET(NOT FLASH) 2- PLC is used in PCS7 to control power turbine(user program done by PCS7 from Siemens ) 3- We don’t have PCS7 software but We have S7 software V5.4 only 4- We have the original user program backup in CD 5- The original backup have PLC properties write protection password (password is unknown for us) Trouble sequence 1-Already battery backup was faulty 2-main power supply lost Result 1- PLC go to stop mode Activates 2- Checking the plc by connecting S7 software and making upload from PLC to PG 3- The uploaded copy have the Hardware configuration but block folder don’t have any block 4- Make PLC memory reset as per Siemens procedure 5- Again Upload from plc to PG but the same result like first upload 6- Trying to download the original backup but when download start the software ask for Password My questions is 1-After I did memory reset how it is asking for password , “NOTE :my original copy showing there is writ protection password” 2-As we use RAM card (not flash) how the uploaded copy still having HW configuration 3-how can I download my original copy Please have a look to the image of our uploaded copyRegards AttachmentHW and RAM.zip (385 Downloads) |