5/31/2011 1:22 AM | |
Joined: 7/2/2008 Last visit: 11/27/2023 Posts: 928 Rating:
|
Hello AlecTek, Is it S7-300/400 PLC or S7-200 or what? Is it a non-configured pressure transmitter? What is the scale inside the transmitter (if it is configurable)? What is the pressure value for 100% level? Best regards. H-H |
Last edited by: H-H at: 5/31/2011 1:29 AM |
|
5/31/2011 1:34 AM | |
Joined: 5/28/2008 Last visit: 12/4/2023 Posts: 4486 Rating:
|
I forgot to tell that the scale function FC105 And unscale function FC106 will be used for S7300/400. If your PLC is S7-200, there are also Scale and Unscale Function you can import their library. Please see the following thread: Scalling for different data fomats with S7-200And also this FAQ: Hope this helps.
|
Ayman Elotaify |
|
5/31/2011 1:59 AM | |
Posts: 95 Rating:
|
Sorry I missed those, It is MP377+ ET200S. The transmitter is non-configured, 4-20mA, range 0 - 100 inch water. The maxium level is 2 meters in a tank. Best regards, Alec |
5/31/2011 2:03 AM | |
Posts: 95 Rating:
|
Hope this helps. Dear Ayman Elotaify, Your post is very useful. I think I understand soemthing now, but I am still not sure - let me read your attachment carefullyand thenquestion you later. Best Regards |
This contribution was helpful to
1 thankful Users |
5/31/2011 2:32 AM |
|
Joined: 5/28/2008 Last visit: 12/4/2023 Posts: 4486 Rating:
|
I have the pleasure to answer you again.
|
Ayman Elotaify |
|
5/31/2011 2:51 AM | |
Joined: 7/2/2008 Last visit: 11/27/2023 Posts: 928 Rating:
|
Hello AlecTek,
Quickly to summarize the links from Ayman Elotaify, -The signal is 4 to 20 mA. -In PLC the signal is read in a word. -the 4 mA gives a zero value in this word -the 20mA gives 27648 decimal value in this word. Now we come to the level, -the transmitter range is 100 inch of water which means 2.54 meters (1 inch= 0.0254 meter) - In your case the 2.54 metersmeasurementisequivalent to 20mA which is equivalent to 27648. - This means that the 27648 will be divided to 10885.04 to give 2.54 which is the maximum height. - In WinCC flexible you can scale the tag. this means that you tell the WinCC flexible if the tag=0 the output on the display is zero and if the tag=2.54 the output on the display is 100%
- V = πr2h V= volume, Pi = 3.14, r= the radius and h= the height which is a maximum 2.54m the 346.657 is a constant that has taken care of Pi, height conversion and volume unit. I hope it's more clear now. If the 346.657 hasn't been cleared yet, please tell me your volume unit. Best regards. H-H |
This contribution was helpful to
2 thankful Users |
Follow us on