Hello everyone I have some questions may anybody answer to me I want to integrate PLC S7-315.2 PN/DP (without CP card) with Yokogawa DCS Centum 3000(ALE 111 card) CPU 315 .2 PN/DP (V2.6) is a type that can support TCP/IP but i could not make a connection with TCP/IP in Netpro Is it possible to communicate? Do i need Cp-341 card? Is it possible to use other protocol instead of modbus-TCP Thanks ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 11/30/2015 12:09:26 PMNew subject after splitting |
|
11/30/2015 8:44 AM | |
Joined: 1/27/2015 Last visit: 7/22/2024 Posts: 53 Rating: (9) |
Dear bird37, you can use the PLC 315 PN/DP with PN Port for Modbus/ TCP. You don't need a CP! The connections are established by using the so called "T-blocks" (T-Con, T-Discon, T-Send, T-Recv). Have a look at the example projects and also the wizard for the comforable parameterizing of the Modbus Parameters. Demo Project: https://support.industry.siemens.com/cs/ww/en/view/103473853 Wizard: https://support.industry.siemens.com/cs/ww/en/view/31535566 License Info: https://support.industry.siemens.com/cs/ww/en/view/103709414
Regards Bachgeist |