4/17/2013 11:28 AM | |
Joined: 1/21/2013 Last visit: 11/20/2024 Posts: 4620 Rating:
|
Hello Raffy, Have a look, Getting Started - Commissioning a CPU 31xC: Counting - Siemens |
Last edited by: Ste39 at: 4/17/2013 11:31 AM |
|
This contribution was helpful to
1 thankful Users |
4/19/2013 10:44 AM | |
Joined: 1/21/2013 Last visit: 11/20/2024 Posts: 4620 Rating:
|
Hi Raffy, look at page 12: Getting Started - Commissioning a CPU 31xC: Counting - Siemens |
This contribution was helpful to
1 thankful Users |
4/19/2013 11:27 AM | |
Joined: 1/21/2013 Last visit: 11/20/2024 Posts: 4620 Rating:
|
Hi Raffy, direction bit is the direction to count up or down, but for the other I would let pulse / direction If you want to connect just one counter pulse (pulse without a direction signal), then you must also select "Pulse / direction". However, the direction input must be at a defined level or not switched, so that no change in direction of rotation can be established. Configuring the "Signal evaluation:" parameter in 31xC CPUs using the technological function "Count" |
Last edited by: Ste39 at: 4/19/2013 11:40 AMLast edited by: Ste39 at: 4/19/2013 11:36 AM |
|
4/20/2013 10:34 AM | |
Joined: 1/21/2013 Last visit: 11/20/2024 Posts: 4620 Rating:
|
Hi Raffy,
The comparison option is the comparison between two values that must be programmed in step 7. Have a look this thread and see Wizard and INS: 313C 2DP counter doesn't count! Hope this help |