6/6/2017 11:04 AM | |
Joined: 10/11/2006 Last visit: 11/6/2024 Posts: 5934 Rating: (815)
|
Dear uel123, The answer to both of your questions is yes. The drive configuration for S110 is done with Starter. When activating Safety via PROFIsafe on S110, PROFIsafe telegram 30 is automatically selected. The telegram will not appear in the telegram configuration. An example for configuring PROFIsafe for S110 is here (chapter 7.2.5): https://support.industry.siemens.com/cs/document/58703073. For the connection to TIA you use GSDML-files. For S110, you find them here: https://support.industry.siemens.com/cs/document/48924746. You drag the correct GSDML-file in your TIA project and configure the telegrams, also PROFIsafe telegram 30 (F-dest.address, watchdog …). Then you can access the Safety Functions as usual. |
With best regards, |
|
This contribution was helpful to2 thankful Users |